DIY home battery storage with an EE degree? Where to find electricians with correct qualfication?

I want to have a ~7kwh home battery storage, they cost more than £4000 (without installation) if I buy an all-in-one solution (inverter + DC batteries in a wall-mounted pack).
Given an EE background, I started digging into what such a system contains, and it turns out only take £2,870 and a server rack to build AC-coupled storage (like building a PC). 

The problem I have is I googled a few battery/solar installers in the Cambridge area, but they only install products with existing dealerships (for cashback reasons?).
I am wondering if additional qualification is required for electricians to install a battery storage system? i.e. if I can hire anyone with an NICEIC certification?

PS: Please shout out if you know where to search or if you want to take the job.

The inverter wiring schematics looks straightforward to me. I understand I probably need an AC and DC switch on both ends of the inverter to be fully compliant.

/cfs-file/A__key/communityserver-components-multipleuploadfilemanager/298edce6_2D00_e269_2D00_4897_2D00_ba7e_2D00_9d909e6ca28d-64262-complete/Manual_5F00_RAI_2D00_3K_2D00_48ES_2D00_5G.pdf

---

In the worst case, can I do it myself?
I know I need to disconnect the consumer unit from the meter (and solar panels), and the CT clamp can't be open-circuited.
But I remember somewhere it is against the regulation to open the consumer unit?

Parents
  • The inverter you show is one of these (click for manual) that uses the direction of current into or out of the grid with the current transformer to decide if the solar panels are exporting and to charge the batteries, or if there is power coming form the grid, to run the batteries down. The wiring of the mains side is straightforward, and any electrician should be able to do that in a regs compliant way to a breaker or RCBO in the consumer unit.

    For the UK the inverter will need to self shut down in the event of a total failure of the external grid, and the instructions capture that, however grey imports  may not be set up for that - some places are less worried about houses exporting power onto a dead street main that may be being worked on. Setting that up and verifying it is working requires a bot of thought, not difficult, but perhaps not something the run of the mill sparks will be familiar with.

    If you anticipate this being a bit of an experiment and do not have one already consider arranging an isolator between meter and consumer unit rather than calling someone out to pull the company fuse or workgin semi-live each time the CU configuration  needs to be changed.

    Also some types of grid tied generation are notifiable to the DNO, as they like to know about things with potential to reverse the voltage drop slope along the street, and this may well fall into that category.

    Mike

Reply
  • The inverter you show is one of these (click for manual) that uses the direction of current into or out of the grid with the current transformer to decide if the solar panels are exporting and to charge the batteries, or if there is power coming form the grid, to run the batteries down. The wiring of the mains side is straightforward, and any electrician should be able to do that in a regs compliant way to a breaker or RCBO in the consumer unit.

    For the UK the inverter will need to self shut down in the event of a total failure of the external grid, and the instructions capture that, however grey imports  may not be set up for that - some places are less worried about houses exporting power onto a dead street main that may be being worked on. Setting that up and verifying it is working requires a bot of thought, not difficult, but perhaps not something the run of the mill sparks will be familiar with.

    If you anticipate this being a bit of an experiment and do not have one already consider arranging an isolator between meter and consumer unit rather than calling someone out to pull the company fuse or workgin semi-live each time the CU configuration  needs to be changed.

    Also some types of grid tied generation are notifiable to the DNO, as they like to know about things with potential to reverse the voltage drop slope along the street, and this may well fall into that category.

    Mike