Spot the minor error here.

No clues.

https://www.youtube.com/watch?v=33XBMj9jHHc

Z.

Parents
  • i noticed the double width SPD had two "L" terminals at the top, and a combined "N" and "PE" terminal at the bottom.

    and no indicator on the front

    I might be wrong, but I presumed that each module was "single pole" - so the double L terminals at the top were handy when looping through the line conductor and then the bottom terminal could be connected to either N or PE depending on the arrangement needed (e.g. CT1 or CT2).

    It seem quite common for type 1 SPDs not to have an indicator - perhaps the spark gap types aren't as liable to failing as the metal oxide varistor usually found in type 2s.

       - Andy.

Reply
  • i noticed the double width SPD had two "L" terminals at the top, and a combined "N" and "PE" terminal at the bottom.

    and no indicator on the front

    I might be wrong, but I presumed that each module was "single pole" - so the double L terminals at the top were handy when looping through the line conductor and then the bottom terminal could be connected to either N or PE depending on the arrangement needed (e.g. CT1 or CT2).

    It seem quite common for type 1 SPDs not to have an indicator - perhaps the spark gap types aren't as liable to failing as the metal oxide varistor usually found in type 2s.

       - Andy.