Energy let-through for Type 2 MCB's ?

I'm nursing an elderly installation containing MK brand Type 2 breakers.

Does anyone have let-through energy curves for MK Type 2 32A MCB ? - Specifically LN5932.

Without any better data I'm likely to expect it to have I^2t no higher then a type C BS60898, and (based on 7x multiplier for instantaneous trip..), perhaps somewhere between a B and  C? Is that a safe assumption? 

I have curves for Wylex BS60898 and for one or two other brands. 

It's a bit of hand-waving I'd sooner not do if there are measured curves somewhere out there?

Parents
  • Anything above 3kA fault current will probably blow the breakers up. They are M3 rated.

    OK do the calculation for a 2kA or 1.5kA  fault current then if you prefer - it's still likely to be more than would reasonably be expected.

    Besides these MCBs are presumably in a CU that has an overall rating of 16kA, so it's probably not a safe assumption that all fault currents will be below 3kA.

    And prey tell please, why do we need the energy let through info. on these domestic sized M.C.B.s?

    Presumably to confirm that reduced c.s.a. conductors meet the requirements of the adiabatic?

       - Andy.

  • And prey tell please, why do we need the energy let through info. on these domestic sized M.C.B.s?

    Presumably to confirm that reduced c.s.a. conductors meet the requirements of the adiabatic?

    I think that the point that Zoomup is making is how often in a domestic installation would you be selecting the conductor size of the CPC? How often would you be wiring in singles?

Reply
  • And prey tell please, why do we need the energy let through info. on these domestic sized M.C.B.s?

    Presumably to confirm that reduced c.s.a. conductors meet the requirements of the adiabatic?

    I think that the point that Zoomup is making is how often in a domestic installation would you be selecting the conductor size of the CPC? How often would you be wiring in singles?

Children
  • As Andy says. And there are a lot of old installations about, often needing judgements, especially for EICR and minor upgrades to poorly structured installations.