Low insulation resistance on remote hager rcbo board and effect on upstream devices.

Was asked to fit an extra skt to kitchen.Old 3036 cu so fit an enclosure with 40A rcd at side of cu.

Had tested IR of ring final earlier and found to be 0.03M.The low reading was traced to a detatched

garage with a 6way hager board spurred off the ring,comprising 6no rcbos with earth leads.The "fault"

as expected cleared when the leads were disconnected.My question is:had there been a greater number

of rcbos in the board or boards, so a lower ir,would the upstream 30ma rcd trip?

Thanks for any replies.

                                                   Hz

Parents
  • I recognise that figure of 0.03Mohms. Strangely, with these RCBO units with loss of neutral I have recorded the same reading whether one or more are in circuit, hardly obeying parallel laws. 

    The connection to the earth bar remains irrespective of the position of the dolly meaning that with a neutral to earth connection in place, any legitimate line to neutral connection will cause a tumble in the line to earth insulation resistance test. 

Reply
  • I recognise that figure of 0.03Mohms. Strangely, with these RCBO units with loss of neutral I have recorded the same reading whether one or more are in circuit, hardly obeying parallel laws. 

    The connection to the earth bar remains irrespective of the position of the dolly meaning that with a neutral to earth connection in place, any legitimate line to neutral connection will cause a tumble in the line to earth insulation resistance test. 