Cooker and shower on the same circuit

Hello everyone,

A few months back, a qualified electrician told me that a cooker and a shower can both be put on the same circuit; that doesn't sound right, surely loads using such a large amount of power must be on their own individual circuits?

I haven't been able to ask a question about this until now because I had difficulty logging into my IET account and had to get a new username and password for it.

Thank you,

Dasa

Parents
  • It depends upon the power of the shower and the cooker!

    Let's say 9 kW shower plus 4 kW cooker. That's 13 kW or 56 A. That would require a 63 A MCB and 16 mm² T&E.

    That leaves two potential problems:

    (1) If you down size the cable at the branching point, you will need overload protection there (433.2.1); or

    (2) If you stay with your 16 mm² T&E, will it fit the terminals?

    Much better to have separate circuits.