Cooker and shower on the same circuit

Hello everyone,

A few months back, a qualified electrician told me that a cooker and a shower can both be put on the same circuit; that doesn't sound right, surely loads using such a large amount of power must be on their own individual circuits?

I haven't been able to ask a question about this until now because I had difficulty logging into my IET account and had to get a new username and password for it.

Thank you,

Dasa

Parents
  • Okay, we can apply diversity for the cooker, what about the shower?

  • Someone may shower whilst the turkey is cooking, but not for long. If they do shower for too long the MCB may trip. No problem, fully protected and safe. You seem to be suggesting something a bit strange Andy, because sub-mains often have more potential loads than the supply, including your house from the DNO I suspect. Mine certainly does, but if I happen to pop the cutout fuse (I don't) is this dangerous or a disaster? As I keep saying, diversity is about time as well as load. Assuming we have a 10mm cable and a 63A breaker, how long can we run at 65A before the cable melts? That is 45A for the shower and 20A for the cooker average BTW, Even worst case the cable temperature will only reach about 71C (Table 4D5A), This is very unlikely however, because this will take about an hour at least, and require a 30C ambient. Lovely Christmas here in Australia!

Reply
  • Someone may shower whilst the turkey is cooking, but not for long. If they do shower for too long the MCB may trip. No problem, fully protected and safe. You seem to be suggesting something a bit strange Andy, because sub-mains often have more potential loads than the supply, including your house from the DNO I suspect. Mine certainly does, but if I happen to pop the cutout fuse (I don't) is this dangerous or a disaster? As I keep saying, diversity is about time as well as load. Assuming we have a 10mm cable and a 63A breaker, how long can we run at 65A before the cable melts? That is 45A for the shower and 20A for the cooker average BTW, Even worst case the cable temperature will only reach about 71C (Table 4D5A), This is very unlikely however, because this will take about an hour at least, and require a 30C ambient. Lovely Christmas here in Australia!

Children
  • That's assuming a 10.00mm2 supply cable of course. I do not think that we have been told the details of this installation. If the existing supply cable is only 6.0mm2 there may be issues.

    Z.

  • Someone may shower whilst the turkey is cooking, but not for long. If they do shower for too long the MCB may trip. No problem, fully protected and safe.

    So in this case we are happy to run the circuit 'hot'?

    particularly in a domestic environment where electrically non-competent families with young children maybe be situated....

    What can one add other than that was not how I was taught.

    Good design removes the possibility of a double fault in later life.