Cooker and shower on the same circuit

Hello everyone,

A few months back, a qualified electrician told me that a cooker and a shower can both be put on the same circuit; that doesn't sound right, surely loads using such a large amount of power must be on their own individual circuits?

I haven't been able to ask a question about this until now because I had difficulty logging into my IET account and had to get a new username and password for it.

Thank you,

Dasa

Parents
  • Well looking a that JB and the CU, what happens next all rather depends on the reason for the call-out. Clearly bears the hallmarks of  the first calibre work of Speedy Bodgitt and Scarper Ltd, but the cable looks in good nick - so if it has been like that for years and that is not the reason you are there, then it is slightly less urgent than if you are called out because there is smoke pouring from the switchgear or folk are reporting it tripping.

    Now you are there to replace the shower - but even if the previous one was the same wattage as the new one, I'd be saying 'aha this is more complex than a direct swap'

    I'd like to think very few would argue against splitting it into two circuits as the best technical solution - clearly it is.
    But given what is already there,  the first act is to fix the problem called out for, only then to improve beyond. This should also involve a conversation with the customer. Do they actually use intend to use both? Maybe leaving it "as is" for now is an option, but in your shoes I'd be wary. Also depends what space is in the box for another MCB, if none then maybe it cannot be split there and then, as that would be a CU change and a world of pain.  If it really cannot be split at the board then a fatter cable from the point of split to the MCB may be nice - but nicer still if the split involved 2 MCB or fuses or one of those mini CUs with an RCD.

    Some things you see do leave you wondering at how other folk decide how to solve a problem,  it reminds me of a shower I found once that had been dobbed into the CU at the main tails, bypassing all fuses and breakers completely.

    As per my first post in this thread 'possible to  do' does not equate to 'it is a good idea'

    Mike.

  • I have seen a few shower circuits dogged into the out going terminals of a consumer unit main switch  more worrying I have seen some dogged into the incoming terminals of the main switch in old rewirable fuse boards which have solid brass busbar connected directly into the main switch, so turning the main switch off doesn't isolate the shower circuit. 

Reply
  • I have seen a few shower circuits dogged into the out going terminals of a consumer unit main switch  more worrying I have seen some dogged into the incoming terminals of the main switch in old rewirable fuse boards which have solid brass busbar connected directly into the main switch, so turning the main switch off doesn't isolate the shower circuit. 