Cooker and shower on the same circuit

Hello everyone,

A few months back, a qualified electrician told me that a cooker and a shower can both be put on the same circuit; that doesn't sound right, surely loads using such a large amount of power must be on their own individual circuits?

I haven't been able to ask a question about this until now because I had difficulty logging into my IET account and had to get a new username and password for it.

Thank you,

Dasa

Parents
  • The IET ELECTRICAL INSTALLATION DESIGN GUIDE Calculations for Electricians and Designers advises in 3.1:

    ”The demand of a circuit or an installation is the current taken by the circuit or installation over a period of time, say 30 minutes”

    and references BS7671 132.3 and 311.1.

    So:

    132.3 Nature of demand

    The number and type of circuits required for lighting, heating, power, control, signalling, communications and information technology, etc shall be determined from knowledge of:

    (I) location of points of power demand

    (ii) loads to be expected on various circuits

    (iii) daily and yearly variations demand 

    (iv) any special conditions, such as harmonics 

    (v) requirements for control, signalling, communication and information technology, etc.

    (vi) anticipated future demand, if specified.

    311.1 Maximum Demand and Diversity

    For economic and reliable design of an installation within thermal limits and admissible voltage drop, the maximum demand shall be determined. In determining the maximum demand of an installation or part thereof, diversity may be taken into account.

    So given that guidance, consider this.

    Last night I pulled off the motorway and stopped at a M&S shop and bought food for our evening meal, I got home and turned on the oven then having started to cook the food I went and had a shower leaving it cooking, then I returned to finish cooking the meal whilst my wife had a shower, the main course needed to cook for 35 minutes, but I left the oven on for the melt in the middle chocolate puddings, so the oven was on for around 45 minutes plus the veg needed cooking as well.

    Therefore if we had a 6 mm circuit protected by a 40 amp MCB supplying both an electric shower and the cooker it would not comply with those regulations, in particular 132.3 (i), (ii) and (iii) because the total demand should be anticipated by the designer, also 311.1 because the thermal limits of the equipment and cable will be exceeded, quite possibly the voltage drop as well.

    Overload should be prevented by design and the circuit protection is not there to compensate for incorrect design.

Reply
  • The IET ELECTRICAL INSTALLATION DESIGN GUIDE Calculations for Electricians and Designers advises in 3.1:

    ”The demand of a circuit or an installation is the current taken by the circuit or installation over a period of time, say 30 minutes”

    and references BS7671 132.3 and 311.1.

    So:

    132.3 Nature of demand

    The number and type of circuits required for lighting, heating, power, control, signalling, communications and information technology, etc shall be determined from knowledge of:

    (I) location of points of power demand

    (ii) loads to be expected on various circuits

    (iii) daily and yearly variations demand 

    (iv) any special conditions, such as harmonics 

    (v) requirements for control, signalling, communication and information technology, etc.

    (vi) anticipated future demand, if specified.

    311.1 Maximum Demand and Diversity

    For economic and reliable design of an installation within thermal limits and admissible voltage drop, the maximum demand shall be determined. In determining the maximum demand of an installation or part thereof, diversity may be taken into account.

    So given that guidance, consider this.

    Last night I pulled off the motorway and stopped at a M&S shop and bought food for our evening meal, I got home and turned on the oven then having started to cook the food I went and had a shower leaving it cooking, then I returned to finish cooking the meal whilst my wife had a shower, the main course needed to cook for 35 minutes, but I left the oven on for the melt in the middle chocolate puddings, so the oven was on for around 45 minutes plus the veg needed cooking as well.

    Therefore if we had a 6 mm circuit protected by a 40 amp MCB supplying both an electric shower and the cooker it would not comply with those regulations, in particular 132.3 (i), (ii) and (iii) because the total demand should be anticipated by the designer, also 311.1 because the thermal limits of the equipment and cable will be exceeded, quite possibly the voltage drop as well.

    Overload should be prevented by design and the circuit protection is not there to compensate for incorrect design.