3 Phase + Neutral 400/230V unbalance:

I came across a circuit drawing for lighting distribution panel 3P+N (400/230V) .

There are 3 phase and 1 phase (Phase to Neutral) loads connected to this Distribution panel. Apparently, there would be unbalance current between the phases due to the single phase loads as it is not connected evenly across all the phases.

Do the breaker trips for the unbalance current due to the current flowing in the neutral? Do I need to increase the earth fault setting? Typically what is the earth fault setting for this configuration? Do I have to care of any other issues associated with it?

Parents
  • AFAIK, 3-phase MCBs don't include the neutral.

    3-phase RCBOs monitor all three phases and neutral. If the three phases are not balanced, it will not trip because the current in the neutral is equal and opposite to the imbalance. In other words, the 4 windings in the RCBO sum to zero.

Reply
  • AFAIK, 3-phase MCBs don't include the neutral.

    3-phase RCBOs monitor all three phases and neutral. If the three phases are not balanced, it will not trip because the current in the neutral is equal and opposite to the imbalance. In other words, the 4 windings in the RCBO sum to zero.

Children
  • But there are 4P MCCBs that do have facility for neutral overcurrent protection (often 0.5x, 1x or 2x the phase conductor setting), which may be what the OP has on the board incomer.

    Normally that only comes into play if you have a reduced neutral CSA, or increased neutral current due to load harmonics.

    As Chris says though, assuming N and E are separate, the earth fault protection is not affected by neutral current / phase imbalance since the sum of currents is still zero.

  • Thats interesting.

    A good few years ago now i remember an electrician friend of mine was a bit worried. 3 phase supply to a pub kitchen with a few guest rooms too.

    He had connector blocks from the 3 phase incommer and was worried that the N should be about three times the csa of the Ls because he had mostly single phase loads. It took some convincing that they do not add up arthithmetically but just vectorally , no harmonics to speak of in this application either.

  • Yep, the peak currents ( or for that matter the R.M.S. currents ) do not all occur at the same time, as they are 120 degrees out of phase with each other...