Bare busbar

How many times have you seen this? 
Busbars indicated dead due to heavy corrosion

Parents
  • “How many times have you seen this” was not referring to how rare it might be, quite the contrary. I have seen this many times but never where a voltage indicator failed on all reference points, line to line, lines to neutral and lines to earth. 

    Electricians roulette, using a two pole tester such as a Megger which gives a single pole voltage indication rather than a test lamp that needs two points of contact should shorten the odds of what I work out to be eighteen tests failing, by finding one live point of contact.

Reply
  • “How many times have you seen this” was not referring to how rare it might be, quite the contrary. I have seen this many times but never where a voltage indicator failed on all reference points, line to line, lines to neutral and lines to earth. 

    Electricians roulette, using a two pole tester such as a Megger which gives a single pole voltage indication rather than a test lamp that needs two points of contact should shorten the odds of what I work out to be eighteen tests failing, by finding one live point of contact.