Insulation Testing during a condition report/periodic test.

I understand why we connect line and neutral together and IR test them to earth. My question is, why not just test line to earth and neutral to earth? It’s just that it’s a bit fiddly connecting line to neutral sometimes.

Cheers 

Parents
  • I would add to mapj1's comment that you may think that you have disconnected all loads, but have missed some electronics somewhere - an aerial booster in the loft, for example.

    So generally a good idea to test on 250 V initially.

  • Thanks for the response, very helpful. 