Insulation Testing during a condition report/periodic test.

I understand why we connect line and neutral together and IR test them to earth. My question is, why not just test line to earth and neutral to earth? It’s just that it’s a bit fiddly connecting line to neutral sometimes.

Cheers 

Parents
  • A pretest at 250V L + N to E . Then if you feel happy with the result you might do the L to E and the N to E.

    Depending upon what you`ve got you might then decide which 500V tests to do.

    Or you might just do the 500V L + N to E (personally I do the 250V test first anyway unless it`s a circuit I`ve just installed)

Reply
  • A pretest at 250V L + N to E . Then if you feel happy with the result you might do the L to E and the N to E.

    Depending upon what you`ve got you might then decide which 500V tests to do.

    Or you might just do the 500V L + N to E (personally I do the 250V test first anyway unless it`s a circuit I`ve just installed)

Children
  • Or we might say that if the R.C.D. isn't tripping off then all is good, and no insulation resistance tests are needed at all!

    Z.