AFDDs NEW REGULATION IN AMD 2

As you may be aware amendment 2 to the 18th Edition was published in the early hours of this morning. If you have the access to the IET Digital package you may have already seen this change.

The new regulation is.

Arc fault detection devices (AFDD) conforming to BS EN 6206 shall be provided for single phase AC circuits supplying socket outlets with a rated current not exceeding 32A in.

High Rise Residential Buildings (HRRB)

Houses in Multiple Occupation (HMOs.

Purpose built student accommodation.

Care homes.

For all other premises, the use of AFDDs is recommended for circuits supplying sockets not exceeding 32A.

So we will not be seeing consumer units full of AFDDs if at all in ordinary domestic premises.

Lights blue touch paper and retires.

JP

Parents
  • Technically, the Landlord Regs say that rented propertied have to comply with BS 7671:2018 at all times (i.e. not :2022), and that any deviations from that which have been flagged by 5-yearly inspections have to be remedied within 28 days.

    So there is currently no legal obligation for landlords of HMO premises to install AFDDs based solely on the the Landlord Regs. If there is some other legal or contractual reason to comply with the latest amendment, than that obviously applies.

Reply
  • Technically, the Landlord Regs say that rented propertied have to comply with BS 7671:2018 at all times (i.e. not :2022), and that any deviations from that which have been flagged by 5-yearly inspections have to be remedied within 28 days.

    So there is currently no legal obligation for landlords of HMO premises to install AFDDs based solely on the the Landlord Regs. If there is some other legal or contractual reason to comply with the latest amendment, than that obviously applies.