Main Protective Bonding to incoming Gas and Water services

Hello,

My query is in reference to regulation 411.3.1.2. 

It is in relation to a project where we have a block of flats where we have a new proposed pumped water supply and an existing Gas supply both either sleeved or installed in poly existing the ground externally to the building. This is then connected to steel/copper pipework run externally up the outside of the block spurring off at each level into domestic properties. Where the meter is located and then onto the domestic installation.

There is a difference in opinion between Client and Contractor parties in relation to the need to bond these pipes after the meter/stopcock positions. The Contractor is disputing the need to install equipotential protective bonding at the point of entry (after the meter/stopcock) within each domestic property, as they believe that because the pipework coming out the ground is not extraneous material, they don’t have to bond it.

The Consultant designing and tendering the project neglected to provide any instruction either way.

The other interpretation sits around the specific words “entering the building” and “at their point of entry” within Regulation 411.3.1.2, which could be considered to be in line with each flat being its own “equipotential zone”, and therefore individual buildings, and that there is a possibility of exporting a potential from one flat into another flat, if those installations are not fully installed to recent versions BS7671, which in this case is very likely, as there are a significant number of leasehold properties within the blocks where most of the electrical installations within, date back to the 1960/70’s. There is also the fact that within most of the properties main protective bonding is already in place (apart from the new water supply).

Any assistance is appreciated.

Parents
  • either sleeved or installed in poly

    thinking further on this. The contractor/designer(s) need to satisy themselves that they aren't extraneous, especially if they are sleeved. Enquiries might need to be made.

    Also, they need to satisfy themselves that they won't become extraneous in the future, ground level rises, and fitting of mechanical metallic protection (possibly where cars park, or bins placed) spring to mind.

Reply
  • either sleeved or installed in poly

    thinking further on this. The contractor/designer(s) need to satisy themselves that they aren't extraneous, especially if they are sleeved. Enquiries might need to be made.

    Also, they need to satisfy themselves that they won't become extraneous in the future, ground level rises, and fitting of mechanical metallic protection (possibly where cars park, or bins placed) spring to mind.