Probably a stupid question...

Right...

We are on a site with 2 onsite substations providing our supplys.

Upon inspection the supply comes from the substation transformer room, into our switch room, as a TP&N feed to our section boards.

We cant see any earth other than the armour of the supply cable which is obviously attached to the section board.

A colleague and I have been debating whether this is a TNS or TNCS supply.???

Given that the transformer is just the other side of the wall in our switch room, and that the earth and neutral must be bonded at the star point of the transformer secondary.

Are we right in thinking the supply is TNS??? 

Parents
  • Yes I would agree with you and record this as a TN-S supply. 

Reply
  • Yes I would agree with you and record this as a TN-S supply. 