This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Safety service

Are smoke/heat/CO detectors connected to the electrical installation in domestic premises a “safety service” as defined in Part 2?

Parents
  • Andy

    Nothing to do with the cable type supplying Safety Service. Emergency lighting, unless the supply is from a Central Battery Service or a UPS, is usually  in T&E.

    For you argument to work a safety Service would be defined by the cable type supplying it rather than as Defined in Part 2 of BS 7671 and the list in Chapter 56.

    And yes to SPDs if you have smoke alarms in your house.

    I think Mark was thinking on his feet when he answered the SPD question on the live webinar. I will have the debate with him when we next meet.

    JP

  • And yes to SPDs if you have smoke alarms in your house.

    Even Grade F1 and F2 which aren't connected to or part of the LV installation?

Reply Children
No Data