Another garden room wiring question

Despite the weather I have built the shell of the garden room and will sooon be ready for the electrician.

We agreed that the SWA would run up the outside of the cladding to a junction box then T+E from there through the cladding and SIP wall, which comprises polyurethane insulation sandwiched between two sheets of OSB. I will be drilling the hole for the cable and would like to run it rhough a pipe, e.g. 22mm plastic pipe. Is that acceptable, if not what else could be used?

Mike

Parents
  • 20 mm PVC electrical conduit? Be aware that significant de-rating may be required.

  • Table 7.1(ii) of the OSG derates 6.0mm² in conduit in an insulated wall to 32 A and this is 32 A circuit. Should be OK?

    Is there anything special about 20mm PVC conduit? I happen to have a lot of 22mm plastic water pipe!

    Mike

Reply
  • Table 7.1(ii) of the OSG derates 6.0mm² in conduit in an insulated wall to 32 A and this is 32 A circuit. Should be OK?

    Is there anything special about 20mm PVC conduit? I happen to have a lot of 22mm plastic water pipe!

    Mike