Another garden room wiring question

Despite the weather I have built the shell of the garden room and will sooon be ready for the electrician.

We agreed that the SWA would run up the outside of the cladding to a junction box then T+E from there through the cladding and SIP wall, which comprises polyurethane insulation sandwiched between two sheets of OSB. I will be drilling the hole for the cable and would like to run it rhough a pipe, e.g. 22mm plastic pipe. Is that acceptable, if not what else could be used?

Mike

Parents
  • 22mm plumbing fittings will not fit electrical boxes so well...  Standard hole sizes are 20mm or 25mm  Apart from that a pipe is a pipe, the wire will not care. A short hop in any sort of tubing will not cause as much derating as a long length. Less than a few inches can be safely neglected,

    Mike

  • Thanks Mike, good point about the fitting. Total length of conduit will only be 150mm so should be OK then.

    Mike

Reply
  • Thanks Mike, good point about the fitting. Total length of conduit will only be 150mm so should be OK then.

    Mike