Main bonding in a split property

I am currently doing an EICR in a large thatched cottage that has been split on to a main house and small rental.

They share one supply but have separate DB's and are on a single TT earth,

They also have a single 30mA RCD protecting both properties, not great for selectivity but at least there is RCD protection.

Main bonding is in place to the oil feed for both properties.

The properties share a single water supply that's bonded when it enters the main property but all the pipework in the second property is giving me a reading of 0.54 ohms. My working assumption is some plastic pipe somewhere along with supplementary bonding to a lighting or power circuit. I believe the pipes just run through the fabric of the building rather than going in the ground but the outer walls of the property are damp, quite a bit of corrosion in back boxes etc, and the pipework is partially buried in the walls in places.

In my mind at least if the walls are damp they are probably also conductive to some extent and providing a path to earth,  I would love to be able to run an insulation test on the pipes but so far I cant find the supplementary bonding to disconnect it.

Ze 47 ohms, Zs at DB 22 ohms.

The MET is more or less diagonally opposite where I would need to make a bonding connection, therefore getting a bond in place is far from trivial.

Would you agree that I probably have no choice and need to find a way to get bonding in place

Is it worthwhile me spending more time trying to locate and isolate the supplementary bonding or is it very likely that an insulation test between the pipes and MET will come back below 22K because of the damp walls.

If I was to make a crimp connection to an existing 10mm earth bonding cable outside and protect it with amalgamating tape would this be acceptable or would I need to give it better protection?

Thanks

Parents
  • sorry Z what is unsatisfactory about it ? - there is a front end RCD - it is TT there always is, every holiday home and caravan in the land has an arrangement like that, people pay over the odds to occupy them,  and they more or less never trip. If it is false trips you worry about it could I suppose be split over multiple RCDs or made a cascade with a 100mA slow feeding a number of 30mA instants in zones. Maybe an odd emergancy light might be worth considering, but really not a big issue.

    Mike.

  • Every holiday home in the land is not TT earthed and has only one R.C.D. Many have multiple R.C.B.O.s I know, I live and work in holiday home land. The whole house (large thatched cottage)  is split into two parts, the second part is let. A build up of natural earth leakage can cause nuisance tripping and the paying guests will not be too pleased. Caravans are small in comparison to this house. The whole installation is liable to the one R.C.D. tripping off and causing domestic outrage, especially if the guests are cooking a meal, heating the home or watching a vital exciting t.v. programme. It's not all about safety Mike, it's also about the reliability of the supply.

    131.1 (vi).

    132.1 (ii).

    314.1.

    www.schofields.ltd.uk/.../

    Z.

Reply
  • Every holiday home in the land is not TT earthed and has only one R.C.D. Many have multiple R.C.B.O.s I know, I live and work in holiday home land. The whole house (large thatched cottage)  is split into two parts, the second part is let. A build up of natural earth leakage can cause nuisance tripping and the paying guests will not be too pleased. Caravans are small in comparison to this house. The whole installation is liable to the one R.C.D. tripping off and causing domestic outrage, especially if the guests are cooking a meal, heating the home or watching a vital exciting t.v. programme. It's not all about safety Mike, it's also about the reliability of the supply.

    131.1 (vi).

    132.1 (ii).

    314.1.

    www.schofields.ltd.uk/.../

    Z.