Lamp post lamp advice needed.

I was asked today to look at several Victorian style lamp posts which are not working. Apparently one out of the 7 works but the lamp is very dim.

I opened the fitting and found the components for a fluorescent lamp, however the lamp itself didn’t look fluorescent. I’m wondering if I should try a like for like replacement of the lamps or should be looking for a different type of lamp? 


Thanks for taking the time to read my question. 


Ben 

Parents
  • Is that incoming brown and black 2 phases then?  - i.e. 400V between wires both sides 230 to ground? Sometimes done on very long runs, as effect of a few volts drop is less on 400V than 230.

    Or it may be 230V of course and just a rather confusing choice of colours. (**)

    I suggest you get your meter out and tell us the voltages wire to wire and wire to ground, both incoming and on the wires going up the pole to the lamp itself, both on the dim one and a dead one.

    And then label it or write in sharpie inside the box.

    Quite right, those LED lamps do not need a ballast, but they do need  the correct 230V, so it may be time to remove the ballast and either connect direct if the incoming is 230V, or track down a 400/230 transformer if it is 2 phase no neutral or find the other end of the supply cable and change it there.

    If the holder is a simple screw in E27 then there has never been a lamp made for which that sort of ballast is correct, it would have beem externally ballasted CFLs that had a plug in base, and in any case either are already phased out, or will be phased out when florry tubes go out of production in the next year or so.

    It can never have been quite right, and the correct thing to fit now is the LED lamps, but please with an un-ballasted 230V supply

    (such errors are not unknown - actually  in the past  I have also seen a lighting tower with ballast at top in the lamp, and also at the bottom, the results were psychedelic, but not helpful. Despite protests 'it had always been like that'  it clearly hadn't.  Wire cutters and some terminal blocks came to the rescue on that one.)

    Mike.

    ** EDIT errata.

    On a larger  monitor the incoming wires look like red and black so that would be pre 2004, and probably 230V but do check for voltage anyway.

    also as Graham notes I am wrong about the ballast type - it is for a SON E - the cheerful orange ones, still made screw in style in the smaller sizes..  https://www.tlc-direct.co.uk/Products/LASONE70slashI.html

  • Quite right, those LED lamps do not need a ballast, but they do need  the correct 230V, so it may be time to remove the ballast and either connect direct if the incoming is 230V, or track down a 400/230 transformer if it is 2 phase no neutral or find the other end of the supply cable and change it there.

    Or fit the correct lamp ... the rating plate on the ballast says 240 V 50 Hz 70 W SON lamp ...

Reply
  • Quite right, those LED lamps do not need a ballast, but they do need  the correct 230V, so it may be time to remove the ballast and either connect direct if the incoming is 230V, or track down a 400/230 transformer if it is 2 phase no neutral or find the other end of the supply cable and change it there.

    Or fit the correct lamp ... the rating plate on the ballast says 240 V 50 Hz 70 W SON lamp ...