Doing an EICR at the moment and fairly sure I have found a ring within a ring, how would you code it?
Protective device 32A MCB and upstream 30mA RCD.
Shortest ring R1+R2 0.17
Longer ring R1+R2 0.54
r1 0.70
r2 0.87
rn 0.72
The short ring has most of the load as it covers the kitchen and fused spur to garage, the longer section is a couple of bedrooms and hallway
Above results to not include fused spur to garage R1+R2 1.10.
Normally I would put a 20A breaker in and code as a C3 but given the loads on the circuit not sure if in this sittuation I would end up with nuisance tripping.
Appreciate your thoughts
Thanks