Short Circuit Current Rating in breakers

Hello 

I have an inquire regarding the short circuit current rating to be determined for the MCCB/RCBO  breakers recently I got to know that  as per the panel manufacturer they have only 10KA not the typical 6KA as used in standard installation (those breakers are used for home appliances/ water heaters/ General sockets) 

is that affect the protection negatively or positively ? 

Thanks

Parents
  • Also check you're comparing like with like - one manufacturer's Icu of 10kA isn't necessarily better than another's Ics of 6kA.

       - Andy.

Reply
  • Also check you're comparing like with like - one manufacturer's Icu of 10kA isn't necessarily better than another's Ics of 6kA.

       - Andy.