12v lighting on a domestic environment

Our 1800s single storey stone cottage was renovated in around 1974.  Since then no work has been done on the electrical installation.  I think a full rewire with new distribution board etc will be called for.

We are prone to rodent infestations in the loft and I am worried that damage done by rodents could cause a fire.  

Given the recent advancements in LED lighting I am considering making the lighting circuits 12v.  I feel this will offer some benefits such as:

Reduced fire risk

Reduced of risk at touch point's (switches)

Possible reduction in cabling costs.

Please can someone advise how using 12v systems in the domestic environment would viewed in terms of compliance with the Wiring Regulations?

Many thanks

Parents
  • I'm not so sure of the advantages of 12V - at one twentieth of the voltage you need twenty times the current to provide the same power - e.g. 12W at 12V is 1A - compared with just 50mA at 240V. So if anything the risk of fire probably increases rather than decreases. In the original part P of the building regs, ELV lighting (with a few exceptions) was notifiable because of these risks. The increased current also means increased voltage drop - so likely to need larger conductors rather than smaller ones. Also you'll likely close the door to some of the safety devices that can reduce those risks - RCDs or even AFDDs. If you're thinking of 12V d.c. then be aware that d.c. arcs are much harder to break than a.c. ones - so in some cases you may need specifically d.c. rated accessories (esp. switches and protective devices).

    If it were me I'd probably just protect the wiring system - e.g. with earthed steel conduit (even flexible steel conduit would do - and not that difficult to install really), with suitable steel boxes behind ceiling accessories. In the old days MICC/pyro wiring might have been another option, but that's pretty rare these days.  Just keep it all on the warm side of any thermal insulation to avoid problems with condensation.

       - Andy.

Reply
  • I'm not so sure of the advantages of 12V - at one twentieth of the voltage you need twenty times the current to provide the same power - e.g. 12W at 12V is 1A - compared with just 50mA at 240V. So if anything the risk of fire probably increases rather than decreases. In the original part P of the building regs, ELV lighting (with a few exceptions) was notifiable because of these risks. The increased current also means increased voltage drop - so likely to need larger conductors rather than smaller ones. Also you'll likely close the door to some of the safety devices that can reduce those risks - RCDs or even AFDDs. If you're thinking of 12V d.c. then be aware that d.c. arcs are much harder to break than a.c. ones - so in some cases you may need specifically d.c. rated accessories (esp. switches and protective devices).

    If it were me I'd probably just protect the wiring system - e.g. with earthed steel conduit (even flexible steel conduit would do - and not that difficult to install really), with suitable steel boxes behind ceiling accessories. In the old days MICC/pyro wiring might have been another option, but that's pretty rare these days.  Just keep it all on the warm side of any thermal insulation to avoid problems with condensation.