This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Induction hob spark fault

Went to a call out. I was told that the induction hob sparked while in use which tripped the RCD. It's a hob and oven on a circuit together. Apparently the same thing happened before (last year I think) so the hob and oven were replaced (student property). Any ideas what may have caused this? The only thing I thought of was loose connections (causing an arc which creates a surge in the hob?). The cooker plate connections were loose so I tightened them. Any other ideas? Maybe:

Loose connections or cable damage (limiting the current flow to the appliance or creating arcs?)

Faulty appliance

Incorrect polarity?

Incorrect voltage?

Thanks.

Parents
  • You could try an ohms range reading but I'm not too sure what you'd get.  If you try and Zs to a  temporary electrode

    1) It is live during that test

    2)  the resistance tells you more about that electrode than the ones that belong to the DNO.

    A normal ohms test is  better than nothing, but try both ways round as it may nor work that well.

    M.

Reply
  • You could try an ohms range reading but I'm not too sure what you'd get.  If you try and Zs to a  temporary electrode

    1) It is live during that test

    2)  the resistance tells you more about that electrode than the ones that belong to the DNO.

    A normal ohms test is  better than nothing, but try both ways round as it may nor work that well.

    M.

Children