EICR coding for no RCD protection in doctors surgery.

Hi All,

    Just wondering thoughts on EICR code for no RCD on any power or lighting circuits in my local doctors surgery. No sockets used for portable equipment outside of course. I coded it C3 6 years ago and strongly advised on a distboard upgrade which was duly ignored they just don't want to spend any money!

Thanks in advance

Rob

Parents
  • The question is whether the medical locations in the practice merit a different code - the requirement for RCD protection in 710.411.4 applies in the same way at home nowadays.

    I think C2, but there may well be a range of opinion in here (as usual).

Reply
  • The question is whether the medical locations in the practice merit a different code - the requirement for RCD protection in 710.411.4 applies in the same way at home nowadays.

    I think C2, but there may well be a range of opinion in here (as usual).