This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EICR coding for no RCD protection in doctors surgery.

Hi All,

    Just wondering thoughts on EICR code for no RCD on any power or lighting circuits in my local doctors surgery. No sockets used for portable equipment outside of course. I coded it C3 6 years ago and strongly advised on a distboard upgrade which was duly ignored they just don't want to spend any money!

Thanks in advance

Rob

Parents Reply Children
No Data