Double pole RCBOs in caravan site

I have a caravan site of around 150 static vans plus 20 touring pitches. Each caravan is supplied from a group pillar via an individual 30mA RCBO but it is single pole. Non compliant, yes, but if you had to call the risk, where would you place it?

Parents
  • If the supply is TT with 2 wires and individual rods at each van, then there is not that much of a risk. to get a high touch voltage on anything other than a van with a fault anyway.

    If the earthing is shared then it is more complex but you would still need a broken neutral to give neutral lift, and an NE fault as well.

    TNS I;d not worry.

    Is the trafo on site ?

    M.,

Reply
  • If the supply is TT with 2 wires and individual rods at each van, then there is not that much of a risk. to get a high touch voltage on anything other than a van with a fault anyway.

    If the earthing is shared then it is more complex but you would still need a broken neutral to give neutral lift, and an NE fault as well.

    TNS I;d not worry.

    Is the trafo on site ?

    M.,