Double pole RCBOs in caravan site

I have a caravan site of around 150 static vans plus 20 touring pitches. Each caravan is supplied from a group pillar via an individual 30mA RCBO but it is single pole. Non compliant, yes, but if you had to call the risk, where would you place it?

Parents
  • Thanks Mike. System is TN-S but distribution cables are hundreds of metres with all sorts of dubious connections. Lost the earth somewhere underground at 3 of the pillars so had to TT them. Loss of neutral is the issue but not on the DNO side as tx dedicated and on site. 

Reply
  • Thanks Mike. System is TN-S but distribution cables are hundreds of metres with all sorts of dubious connections. Lost the earth somewhere underground at 3 of the pillars so had to TT them. Loss of neutral is the issue but not on the DNO side as tx dedicated and on site. 