  • OSG EICR 

    Observation 3- No additional protection by RCD for socket-outlets C3

    Inspection Schedule- 5.12 Provision of additional protection by RCD not exceeding 30 mA.

    • for all socket outlets of rating 32A or less, unless an exception is permitted. Ticked acceptable condition.
    • for supply to mobile equipment not exceeding 32 A for outdoor use. Ticked acceptable condition.
    • for cables concealed in walls at a depth of less than 50 mm . C3 Improvement recommended.

    There is no rhyme or reason to it, the schedule doesn’t tally with the observations, the observations comment on the sockets, but not the cables in walls, the schedule codes the cables in walls but not the sockets.

Reply
  • OSG EICR 

    Observation 3- No additional protection by RCD for socket-outlets C3

    Inspection Schedule- 5.12 Provision of additional protection by RCD not exceeding 30 mA.

    • for all socket outlets of rating 32A or less, unless an exception is permitted. Ticked acceptable condition.
    • for supply to mobile equipment not exceeding 32 A for outdoor use. Ticked acceptable condition.
    • for cables concealed in walls at a depth of less than 50 mm . C3 Improvement recommended.

    There is no rhyme or reason to it, the schedule doesn’t tally with the observations, the observations comment on the sockets, but not the cables in walls, the schedule codes the cables in walls but not the sockets.