I think the MCCB panel or BS88 s fused isolators are your only option - I doubt you'd get bigger than a 63Amp MCB for a 250A Distribuion board.
Perhaps go MCCB panel board - SWA - to a metal clad 3 phase appropriately sized Isolator - into which the oven is connected. A commando socket is also a possibility. An isolator is cheaper than a fused isolator. You can rely on the MCCB in the MCCB panel for overload protection.
I think the MCCB panel or BS88 s fused isolators are your only option - I doubt you'd get bigger than a 63Amp MCB for a 250A Distribuion board.
Perhaps go MCCB panel board - SWA - to a metal clad 3 phase appropriately sized Isolator - into which the oven is connected. A commando socket is also a possibility. An isolator is cheaper than a fused isolator. You can rely on the MCCB in the MCCB panel for overload protection.