Cable Standards and Selection

Hi 

Would be grateful for some guidance on cabling standards/selection

Currently developing an large energy storage system and equipment is coming from all over the place.

I seem to be struggling to get European suppliers of equipment to comply with British standard cabling such as shown in Table 4A3. I keep on getting thrown all sorts of weird and wonderful cable datasheets, all with IEC standards but no ref to BS or BS EN that I am comfortable or familiar with. We have clearly specified BS7671 as the standard to be followed but there seems to be a reluctance to adhere to this.

Example

Power cables 2XY-fl RM 2x2,5mm² (bk)

Instrument cables   RE-2X(St)Yv-fl 1x2x1.0mm² (bk/bu)

Would other non BS cables be accepted in the UK and signed off and what are the implications in not following cable recommendations in table 4A3? 

kind regards

Chris

Parents
  • See also Regulations 511.1 (including Notes 1 and 2) and 511.2 (including Note).

    There is more paperwork to be done ("justification" as per 511.1 and 511.2) where the cable is not to a British or Harmonized standard (usually numbered "BS", "BS EN", "BS IEC", "BS EN IEC" etc.).

    The use of the particular cables (preferably with a reference to the justifications) should be included on the electrical certificates ...

Reply
  • See also Regulations 511.1 (including Notes 1 and 2) and 511.2 (including Note).

    There is more paperwork to be done ("justification" as per 511.1 and 511.2) where the cable is not to a British or Harmonized standard (usually numbered "BS", "BS EN", "BS IEC", "BS EN IEC" etc.).

    The use of the particular cables (preferably with a reference to the justifications) should be included on the electrical certificates ...