Cable for ELV lighting application

Please can anyone give me advice on cable selection for an ELV (24V) LED lighting tape application?

The tape is the RGB+W type, i.e. 5 conductor, rated at 19.2W/m. I want to install a 5m run, which would amount to 96W and hence draw 4A. For the ELV driver-to-tape connection, the manufacturer supplies 5-core PVC flex to ISO 6722-1:2011 Class B, which is the standard for Road Vehicle wiring, 60 or 600V (60V in this case). This cable has 0.5 sq.mm copper cores (16 x 0.2mm dia), to BS EN 60228:2005, a max operating temp. of 105 deg.C,and a nominal current rating of 11.0A, according to the manufacturer's data sheet.

A quick glance at Table 4F3A tells us that 0.5 sq.mm flexible cable of any temperature rating over 60 deg.C has a current capacity of 3A (AC - for some reason this table doesn't specify DC, anyone know why?) This type of flex would presumably be made to BS 7919, but the copper is still to BS EN 60228, which would suggest to me that the current carrying capacity would be much the same for any cable made using this copper wire, regardless of the cable standard.

I cannot see this cable carrying 11 Amps for a long and happy service life; but my question is this: can I rely on it to carry the 4A in my application, and would it comply with table 52.3 and 715.524.201, which are rather vague?

Many thanks,

Rob

Parents
  • This type of flex would presumably be made to BS 7919, but the copper is still to BS EN 60228, which would suggest to me that the current carrying capacity would be much the same for any cable made using this copper wire, regardless of the cable standard.

    For most cables, the limiting parameter is the insulation material rather than the conductor. PVC type compounds degrade gradually with heat and time - the hotter a cable is run the shorter its useable lifespan. For fixed wiring we typically expect a cable to last 70+ years - which it does when the conductor temperature is limited to around 70 degrees max (depending on duty cycles etc). For vehicles the expected service life is closer to 10 years - so the conductors can run much hotter and the resulting reduction in lifespan by nearly an order of magnitude is acceptable

       - Andy.

Reply
  • This type of flex would presumably be made to BS 7919, but the copper is still to BS EN 60228, which would suggest to me that the current carrying capacity would be much the same for any cable made using this copper wire, regardless of the cable standard.

    For most cables, the limiting parameter is the insulation material rather than the conductor. PVC type compounds degrade gradually with heat and time - the hotter a cable is run the shorter its useable lifespan. For fixed wiring we typically expect a cable to last 70+ years - which it does when the conductor temperature is limited to around 70 degrees max (depending on duty cycles etc). For vehicles the expected service life is closer to 10 years - so the conductors can run much hotter and the resulting reduction in lifespan by nearly an order of magnitude is acceptable

       - Andy.