New R.C.D.s and TT Earthed Installations.

Good morning all on this lovely sunny morning.

I was wondering if we need to notify all of our customers with TT earthed installations of the need to remove any AC type R.C.D.s and replace them with the newer type A, B or F? The renewal will be to ensure correct operation if unknown loads are connected with a D.C. component.

LLLLLLLLLOOOOOOOOOOOOOOOOOOOOOOoooooooooooooooooooooooooooookkkkkkkkkkkkkkkkkkkkk

www.youtube.com/watch

Z.

Parents
  • I was wondering if we need to notify all of our customers with TT earthed installations of the need to remove any AC type R.C.D.s and replace them with the newer type A, B or F?

    Was this any different to telling them their old VOELCB was no good and they needed to be swapped out for RCDs in the first place (or as some sparks did, try and make TN-S by connecting to the supply cable metallic sheath/armour)?

    Worth also considering you might need to tell customers you don't know how effective their older BS 4293 or BS 7288:1990 RCDs are in any case, regardless of DC components, because they didn't undergo the same EMC testing that's now included in the product standards, so they just might not operate when needed?

    I guess action as advised by whichever guidance on "coding" you subscribe to?

  • I still come across the good quality old Voltage operated earth leakage circuit breakers that still work perfectly if the earth wire or rod hasn't rotted away. The Chilton and Crabtree units were made to a very high standard. Some date back to the 1960s.

    Some TT sites have dozens of pitch hook ups, the upgrading will cost thousands of pounds and may put the site owners out of business.

    Please provide any proven examples where an E.M.C. problem  has prevented an old non electronic R.C.D. from working correctly and causing a hazard.

    Z.

  • Please provide any proven examples where an E.M.C. problem  has prevented an old non electronic R.C.D. from working correctly and causing a hazard.

    The qualification doesn't work that way ... it works the other way, in terms of placing products on the market that are certified by the manufacturer according to the legislation.

    At present, there is no proof one way ... or the other, regarding the "failure" of RCDs under given circumstances (although there is quite a bit of anecdotal evidence of unwanted tripping that is, on the balance of probabilities, caused by "EMC issues").

    However, there is a complete absence of evidence that the older products meet the same requirements as newer products ...

  • I can provide impirical evidence that a lot of older devices still operated reliably. In fact being so large, mechanical and clunky they are certain not to be affect by E.M.C. concerns. I am sure that others can provide evidence of older devices still being fully operational as well.

    Edit. Add.....this is a good booklet that explains the operation of the old earth leakage circuit breakers and show the construction of them. It is historical but well worth a read.

    www.ebay.co.uk/.../354069837068

    Z.

Reply
  • I can provide impirical evidence that a lot of older devices still operated reliably. In fact being so large, mechanical and clunky they are certain not to be affect by E.M.C. concerns. I am sure that others can provide evidence of older devices still being fully operational as well.

    Edit. Add.....this is a good booklet that explains the operation of the old earth leakage circuit breakers and show the construction of them. It is historical but well worth a read.

    www.ebay.co.uk/.../354069837068

    Z.

Children
  • I can provide impirical evidence that a lot of older devices still operated reliably.

    I'm not saying problems are "guaranteed", but more importantly, safe operation of devices as we know it today is not proven by undergoing the same type testing ... and that's all we do know for sure.

    In fact being so large, mechanical and clunky they are certain not to be affect by E.M.C. concerns.

    Including the effect of harmonics and DC currents (EMC is conducted as well as radiated)?

    Edit. Add.....this is a good booklet that explains the operation of the old earth leakage circuit breakers and show the construction of them. It is historical but well worth a read.

    I like that sort of thing.

    VOELCBs in there too? These were another thing entirely, and phased out due to nuisance operation.

  • Yes, I know about the problems with Voltage Operated Earth Leakage Circuit Breakers. These days with plastic mains water pipes the problem may not exist of fault currents in one house tripping the unit next door.

    Z.

  • Here is a quick introduction from a couple of mates that I met in the Dog and Duck recently...................

    https://www.youtube.com/watch?v=yxbshDyGPng

    Z.