This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

EV Chargers with built in RCD and 537.2.2

I read 537.2.2, and wonder if this applies to our EV charge points which offer built in 30ma and 6ma DC RCD's. Im sure these RCD must be electronic in nature. 

Upstream is a traditional MCB, so the EV Charger could be isolated.

However looking at 411.3.2.1 it has the line "the protecticve device shall be suitable for isolation of at least the line conductor"

So as 411.3.2.1 uses the term isolation, and the RCD is a protective device, should the inbuilt RCD comply with 537.2.2?

I'll stop reading the regs and have a cup of T, Thank you for looking, and in advance of your advice.

Parents
  • Well, RCDs for EV charging equipment must disconnect all live conductors (722.531.3.1).

    In addition, the RCD must comply with at least one of the following standards (722.531.3.101):

    • BS EN 61008-1
    • BS EN 61009-1
    • BS EN 60947-2
    • BS EN 62423

    Devices to each of these standards may perform isolation function (see Table 537.4). "Electronic" RCDs must still comply with the standards, which includes constructional standards, and a requirement for a test facility, etc. - which means if the RCD doesn't have all these things, you need a physical RCD up-front.

    With respect to individual charging points, perhaps the best place to get the answer to the question is the manufacturer. I have seen charging equipment that does have physical RCDs to the above standards installed.

    Incidentally, the RCD may be "backed up" by an RDC-DD to BS IEC 62955 (see also 722.531.3.101) which is a whole other set of considerations.

Reply
  • Well, RCDs for EV charging equipment must disconnect all live conductors (722.531.3.1).

    In addition, the RCD must comply with at least one of the following standards (722.531.3.101):

    • BS EN 61008-1
    • BS EN 61009-1
    • BS EN 60947-2
    • BS EN 62423

    Devices to each of these standards may perform isolation function (see Table 537.4). "Electronic" RCDs must still comply with the standards, which includes constructional standards, and a requirement for a test facility, etc. - which means if the RCD doesn't have all these things, you need a physical RCD up-front.

    With respect to individual charging points, perhaps the best place to get the answer to the question is the manufacturer. I have seen charging equipment that does have physical RCDs to the above standards installed.

    Incidentally, the RCD may be "backed up" by an RDC-DD to BS IEC 62955 (see also 722.531.3.101) which is a whole other set of considerations.

Children