Formula for values in Table 52.2 - cables passing through thermal insulation?

Does anyone know the formula used to get the values given in table 52.2 BS7671, (now moved to Appendix 4 item 2.6) please? 

Not how to apply the values, this is obvious.

Many thanks

Ben

  • This was dealt with by an IEE Wiring Regulations committee called WR2.  I was on WR2 as the NICEIC representative in the early 1990's.

    This table was reviewed by WR2 but , as I recall, the data came to WR2 via ERA Technology Ltd.  I pretty sure the data was mainly produced from experiments and I don't recall any formulas.

    Regards

    Geoff Blackwell 

  • Many thanks Geoff, great to have access to first hand information from yourself.

    Cheers

    Ben

  • As Geoff says this was done by experiment. I carried out some early work at Pirelli in the late 70s. This was prompted by my father who was on the wiring regulation committee. The first trials were with a model plasterboard and joist ceiling and a selection of different insulating materials. A number of different cross sections of T&E were used.

    These trials showed that there was a possible problem and the work was passed on for more precise measurements to be made. I think I still have a copy of my original report.

  • Hi Roger, 

    Many thanks for the response. Amazing that you might even have a copy of the old report!

    Cheers

    Ben