Surface mount junction box and pull switch

I need to surface mount a 4 terminal junction box & pull switch with plastic trunking, I don’t like using the cheap junction boxes (or plastic trunking) but it needs to be white as it’s on a ceiling.

I’ve got the fire clips for the trunking, but does the cable need to be secured in the JB and pull switch?  

Parents
  • Not in my view as the lengths are presumably very short and therefore very unlikely to present an entanglement or entrapment risk for escapees or fire fighters.

  • the longest run is 2m which I will clip to the joist though the trunking, it is a strange setup as each light has its own pull switch (after the wall switch) so they can be turned off if not required  

    Its a small shop so that's been modified over the years

Reply
  • the longest run is 2m which I will clip to the joist though the trunking, it is a strange setup as each light has its own pull switch (after the wall switch) so they can be turned off if not required  

    Its a small shop so that's been modified over the years