Generator Earthing (Neutral Earthing loop between other nearby Generators).

In one of our recent project. There are multiple generators and individually feeding to each MDBs. Consultant instructed to loop all the Generator Neutral between each generators. Our proposal to provide individual neutral earthing for each generators. 

Is it advisable to loop Generator Neutral Earthing (These generators are not synchronizing)

Parents
  • In a TN-S system, or TN-C-S downstream of the "split" of PE from N, BS 7671 (and IEC 60364-4-44 section 444) does not permit multiple N-PE connections to be made at any one time. It is not good for EMC, and also may lead to unwanted tripping of RCDs.

Reply
  • In a TN-S system, or TN-C-S downstream of the "split" of PE from N, BS 7671 (and IEC 60364-4-44 section 444) does not permit multiple N-PE connections to be made at any one time. It is not good for EMC, and also may lead to unwanted tripping of RCDs.