Local Isolation - Electric Windows

Hi all,

Advise please…..

Customer lIves in a bungalow and is removing the ceiling in her kitchen to make a double height vaulted ceiling. 

She is having electric velux windows installed, normally I would install a switched fused spur adjacent to the velux, 

Can I put the fused spur it in the loft space where we have a nice new wall with all the Boiler, PV system, TV amp etc mouthed, would locating it there be deemed local isolation for the electric windows?

If I did mount it adjacent to the velux’s it would be 3.3m off the ground. Hardly easy to isolate and probably contravening CDM regs.

And the customer doesn’t want sockets on show around the kitchen so is having things like boiling hot water tap, intergrated microwave etc, and wants only three sockets hidden under the pelmet of her cupboards. 

thanks

Parents
  • Generally if an isolation device is remote from the equipment it's meant to isolate then it needs to be able to be locked off - not all designs of FCU  have that facility. Also for TT systems the N needs to be isolated as well as L - which probably can't be achieved by locking out the fuse carrier.

       - Andy.

  • And if there is smoke coming out of the equipment the isolation device needs to be easily located and must be obvious in use. (Clearly labelled).

    460 (i).

    And we need to consider switching off for mechanical maintenance as well 464.1.

    Z.

Reply
  • And if there is smoke coming out of the equipment the isolation device needs to be easily located and must be obvious in use. (Clearly labelled).

    460 (i).

    And we need to consider switching off for mechanical maintenance as well 464.1.

    Z.