This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Local Isolation - Electric Windows

Hi all,

Advise please…..

Customer lIves in a bungalow and is removing the ceiling in her kitchen to make a double height vaulted ceiling. 

She is having electric velux windows installed, normally I would install a switched fused spur adjacent to the velux, 

Can I put the fused spur it in the loft space where we have a nice new wall with all the Boiler, PV system, TV amp etc mouthed, would locating it there be deemed local isolation for the electric windows?

If I did mount it adjacent to the velux’s it would be 3.3m off the ground. Hardly easy to isolate and probably contravening CDM regs.

And the customer doesn’t want sockets on show around the kitchen so is having things like boiling hot water tap, intergrated microwave etc, and wants only three sockets hidden under the pelmet of her cupboards. 

thanks

Parents
  • Do the Manufacturers Instructions say that local isolation is required? If not I suggest you do not fit it, this is gilding a lily that useless. If someone wants to work on the electrics, we have perfectly good rules for isolation. The "its on fire" situation is not going to change by isolating it locally and no one is going to find a ladder! This is the place for the main switch being accessible and known.

Reply
  • Do the Manufacturers Instructions say that local isolation is required? If not I suggest you do not fit it, this is gilding a lily that useless. If someone wants to work on the electrics, we have perfectly good rules for isolation. The "its on fire" situation is not going to change by isolating it locally and no one is going to find a ladder! This is the place for the main switch being accessible and known.

Children
No Data