Addition of a new circuit............

In the wake of the new webinar on inspection and testing, is it still compliant to add a new circuit to an existing plastic consumer unit fitted with type A/C RCD protection and nothing else?

How much 'engineering judgement' leeway do I actually have?

Parents
  • If the new circuit requires a type A (e.g. because it has sockets or a known load with electronic components) then protecting it with a type AC isn't compliant with BS 7671 amd2 - there's no leeway there. On the other hand, being plastic is not an issue.

  • But if an appliance becomes faulty with an earth fault, unless the system is TT, the overcurrent protective device will still disconnect the faulty appliance.

    Z.

  • So? Normally RCDs are required for additional protection rather than fault protection. A nail in the wall contacting just the L conductor won't cause an overcurrent, but may still kill you if you touch it, unless an RCD trips. And hopefully that RCD isn't being blinded by DC leaks or faults.

  • Banging a nail into unknown territory is stupid. It is just like tombstoning, i.e. jumping into unknown water that may have hidden dangers. Fatality by banging the nail into a wall and connecting with a line conductor MAY kill somebody, but largely depends upon how well they are earthed. Probably if they are standing on an insulating wooden floor or carpet they will just get a reminder of how stupid they have been. There are not many reported deaths regarding this scenario.

    SOLUTION. Don't bang nails into walls that may contain pipes or cables.

    Z.

Reply
  • Banging a nail into unknown territory is stupid. It is just like tombstoning, i.e. jumping into unknown water that may have hidden dangers. Fatality by banging the nail into a wall and connecting with a line conductor MAY kill somebody, but largely depends upon how well they are earthed. Probably if they are standing on an insulating wooden floor or carpet they will just get a reminder of how stupid they have been. There are not many reported deaths regarding this scenario.

    SOLUTION. Don't bang nails into walls that may contain pipes or cables.

    Z.

Children
  • You seem to be saying that we don't need to install RCDs for additional protection as only stupid people would be killed by their lack?