This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

derating multiple trefoils

I need to determine number of cables in trefoil

2783A total

240mm2 90C (terminations OK for 130C) flexible

unbalanced so have neutrals

50% earth

2 layers of trefoils. 6 3 phase + 2 neutral + 1 earth = 27 cables (9 trefoils)

 6 sets 607 x .91 x..86 x .97?

Manufacturer says use 775 x 0.91 4sets

Please advise

Also IEC60364 has no 0.97 flexible cable de-rating factor....

Kindest regards

Parents
  • And of course the loading - is the full load on 24/7 or is it much lower with occasional busts of full load ?

    Mike.

  • Data centers so load is pretty constant at about unity P.F.

Reply Children
No Data