Hi All,

EN60204 states: "The connection of two or more conductors to one terminal is permitted only in those cases where the terminal is designed for that purpose." Does anybody know whether this prohibits the use of standard twin ferrules (where two wires are crimped into a single ferrule) or whether the assembly of two wires and a ferrule is somehow considered to be a single conductor in the eyes of the standard?

Twin ferrules seem to be commonly used in machine building, often with claims of compliance with 60204. I was expecting to find some easily accessible guidance/knowledge/definitions regarding this situation but my web trawl hasn't found much.

Any wisdom will be gratefully received. Thanks.

Parents
  • Only thing I can add is, a twin ferrule is designed for 3 terminations, two in, one out.

    I think the design of the terminal is what is relevant, and what type of cable it accepts, eg  solid, stranded, fine wire, and whether it is designed to accept two of the above. 

    An MCB cage clamp is designed to accept two ring circuit conductors for example, and at a push a spur fed from it too.

Reply
  • Only thing I can add is, a twin ferrule is designed for 3 terminations, two in, one out.

    I think the design of the terminal is what is relevant, and what type of cable it accepts, eg  solid, stranded, fine wire, and whether it is designed to accept two of the above. 

    An MCB cage clamp is designed to accept two ring circuit conductors for example, and at a push a spur fed from it too.

Children
No Data