EN60204 and twin ferrules
Hi All,
EN60204 states: "The connection of two or more conductors to one terminal is permitted only in those cases where the terminal is designed for that purpose." Does anybody know whether this prohibits the use of standard twin ferrules (where two wires are crimped into a single ferrule) or whether the assembly of two wires and a ferrule is somehow considered to be a single conductor in the eyes of the standard?
Twin ferrules seem to be commonly used in machine building, often with claims of compliance with 60204. I was expecting to find some easily accessible guidance/knowledge/definitions regarding this situation but my web trawl hasn't found much.
Any wisdom will be gratefully received. Thanks.
  • Dave in the Shed,
    No problems sharing my thoughts, below is a image of a terminal linking assemby that I and others would call a honecombe type this being more for terminals than MCB's, but you are spot on principal is the same.
    Cheers GTB
  • Ah yes - I know these well.
    Thanks.
  • I've seen those terminal linkers referred to as 'comb' (like hair do) , but in my world honeycomb is lots of tubes formed into hexagons. Used to keep RF and EMPs out of the cooling ducts but allow almost laminar air flow. Depending who you talk to, be aware that there may be potential confusion with the honey ;-)
  • The EN 60204 compliance is assured because a dual "bootlace ferrule" is exactly designed to make 2 single wires into a single item for the clamping screw. I think that the 2 wires part comes from bolt lockdown where conductors form a loop under a washer and nut. 2 loops are obviously not a stable arrangement. Bootlace ferrules are designed to hold the core of a fine wire cable together and to prevent damage to the fine wires, in something like a chocolate block type of connection. A double bootlace simply holds the fine wires of 2 or more (given suitable size) fine wires together so that they are all correctly aligned and clamped by a single screw. I have never seen this arrangement (given a properly crimped ferrule) fail.
    As you can see above they come in big sizes, that one is 25mm2, and much better for tails than even the more flexible type as shown
  • I am not aware of anything published, but here are three ways of looking at this.
    (1) Let's say that the double ferrule is at the supply end of a cable. The portion that is within the metal part of the ferrule is one conductor, albeit of, say 14 strands. The fact that it promptly splits into two each with its own sheath immediately afterwards does not change the matter.
    (2) If you remove the ferrule from the terminal, how many conductors do you have? Answer = 1.
    (3) If you carefully remove 20 mm of insulation from a cable, bend it through 180°, and insert it in the ferrule, have you suddenly made two conductors out of one. Of course not!
    HTH and good luck!
  • Thank you David - the body of agreement continues to grow.
    When you say that 60204 compliance is assured, is that based upon what your experience as a mighty fine engineer tells you in your own interpretation of 60204 or is it based upon some published official guidance that I've yet to locate? Not that I'm doubting your opinion of course!
    I'm still slightly cautious because there does seem to be a minority who forbid the use of twin ferrules in the land of 60204 and I don't want to rely upon the occasional twin ferrule only to have a splendid bespoke machine rejected by an over-zealous compliance officer at a client's premises. If only there was some sort of official clarification which I could wheel out in such an eventuality. It strikes me that there is justifiable reason for the definition of "conductor" (as used in the 60204 clause relating to the 1 wire/2 wire issue) in the preamble of 60204 to be extended to refer to twin ferrules.
    So much discussion about the humble ferrule - who'd have guessed....
  • Thanks again.
    All useful examples of good reasons why the twin ferrule should be allowed to exist and not be banished to to the world of forbidden things that once were useful to sensible people. I think that I now have a pretty good armoury of reasoning to confront any ferrule jobsworth.
  • Dave in the shed,
    I dont think you will get a definitive clarification etc. It is like thousands of other regs and standard items where it is down to one's interpretation. I think everyone on this thread is interpretating EN60204 and connections into terminals the exact same. Like you meeting an over zealous QA inspector that indicates otherwise is in my opinion reading the satement wrong. Two conductors are terminated correctly in the twin ferrule, and to comply only one "Conductor" the pin of the cable lug or twin ferrule is clamped in the terminal, the satement is about the terminal.
    GTB
  • Thanks GTB - nicely summarised.
  • Weidmueller, amongst others, specify the min max conductor sizes specifically for twin conductor bootlace ferrules for use with their terminal blocks. Notably the sizing is sometimes different to that for singles, presumably because the ferrule is larger to accommodate the second conductor.