Excel input for 7671 calculation

Could any one assist this old duffer? I have successfully put together a fairly comprehensive circuit calculation spreadsheet in Excel for circuits up to and including 16mm2. However, can anyone advise how I can enter a cell instruction to convert Cos theta to the sine of the angle. For example power factor is 0.8 and sine of same angle is 0.6. All I want to do is enter 0.8 into a cell and the corresponding cell correctly inputs 0.6. 

Parents
  • Good to see that we all agree on pythag.

    But could you explain your 'core drop' comment please ?

    Do we need to consider neutral drop ? surely only for an out of balance term ?

    or is it a star/delta thing ?

    Say if we have a 230/400V 3 phase supply,  with a balanced 10V drop,

    I would read that to be 10V off each phase,(so a drop of 1/23) so it becomes 220/ 382 .

    Do others  understand it to be   a 10V drop phase-phase (so a drop of 1/40) so 226 /390?

    M

  • If you run through the formula it gives the voltage drop in volts along one straight length of single core cable. Thus the coefficient b that they refer to needs to be multiplied by 2 for single phase. Now they say it only needs to be multiplied by 1 to get the three phase voltage drop. That would only be the voltage drop along the single core and the line voltage would be root 3 that value.

Reply
  • If you run through the formula it gives the voltage drop in volts along one straight length of single core cable. Thus the coefficient b that they refer to needs to be multiplied by 2 for single phase. Now they say it only needs to be multiplied by 1 to get the three phase voltage drop. That would only be the voltage drop along the single core and the line voltage would be root 3 that value.