Hi all,
Currently have a motor incorporated into a fan oven, however the only electrical protection on the power circuit is an MCB. to a contactor.
552.1.2 states:
"Every electric motor having a rating exceeding 0.37kW shall be provided with control equipment incorporating means of protection against overload of the motor. This requirement does not apply to a motor incorporated in an item of current using equipment complying as a whole with an appropriate British or harmonised standard"
Annex A53, table TA53.1 says that a circuit provides overload protection
Is this all the standard wants, an MCB with the thermal overload component? Or is it talking about a separate overload relay added on to the contactor? Obviously a 10A MCB won't begin to operate until current is 14/15A
Thanks