Good day all
For this example: Ib 32A, OCPD 63A BS88 , 10mm2 SWA @ 70DegC 0.5m direct buried (other stuff inc. soil conditions all at unity/not applicable/as tabled and so on)
Iz = It * (correction factors)
68.6 = 60 * 1.1 * 1.04
the Ib <= In <= Iz ...
32 <= 63 <= 68 [tick]
the I2 <= 1.45 Iz ... (R433.1.203)
In <= 0.9 Iz
63 <= 61.7 [cross]
In the example scenario, 10mm2 SWA wont do. A jump up to 16mm2 will be required.
Q1) is this non-rigorous assessment correct ?
Q2) the cable cost increase is not negligible for the sake of measly ~2 Amps, is something missed or is there a more rigorous approach (factors, experience, in reality etc) to be able to use 10mm2 and still comply with Regs, or is it done with ?
Regards Habs