Simplified guide to cable sizes for overseas DIY installation.

I have been asked to suggest a very simple guide as to what size cables should be used for DIY installations overseas, in a hot location. This must be kept simple without the complications of de-rating for grouping or for high ambient temperatures.

I appreciate that the best advice in say the UK is "have the work done by a suitably qualified electrician" This advice is however for locations were allegedly qualified electricians are hard to find and often seem to lack basic competence.

I have therefore suggested the following.

Lighting circuits use 1.0mm cable on a 5 amp or 6 amp fuse. Earthing/grounding required if metal switches or fittings are used, but otherwise is recommended, not obligatory.

General purpose small power use 2.5mm cable on a 15 amp or 16 amp circuit. connected to a number of socket outlets of whatever type is used locally.

Dedicated circuits for larger loads, most likely water heaters, cook stoves, and air conditioners.

For a running current not exceeding 13 amps use 2.5mm cable from a 15 amp or 16 amp circuit.

For running current over 13 amps and up to 18 amps use 4mm cable on a 20 amp fuse.

For running current more than 18 amps and not exceeding 27 amps, use 6mm cable on a 30 or 32 amp fuse.

I consider that these loadings have a large enough factor of safety that no calculations are required for high ambient temperatures. Likewise modest numbers of cables grouped together will be fine at the above ratings. No allowance made for voltage drop, as the above will be fine for modest sized homes. No allowance made for different cable types, as in practice it will be whatever the local shop has in stock.

Earth loop impedance not relevant as no one knows what the earthing system is, if any,  and I doubt that anyone has an earth loop tester.I urge use of a front end RCD and a local earth rod. Colour code in line with whatever is used locally.

Parents
  • Actually, I expect it might surprise some of the younger qualied gang in this country the things that were commonplace here not that many years back. Ironing from an iron that was plugged into a BC lampholder just for starters

  • Indeed, how did we all survive ? but it is a good few years , we are getting older. Earth pins on all new power sockets from about 1939, on all new lights circuits from about 1969, but these regs changes   take about half a century to work through to be common in  almost all installations in the UK.
    I was in my teens when I last fitted a 2 pin plug to something, to allow use with an existing  pre-war socket, and I'm only in my 50s - well the 2nd half of them. (one of the BS 73 type with split pins - though even in the  1970s it took me a while to find someone that still had one  -  images of the kind of thing on flame port - incorrectly listed there as BS 372 - that was a later 2 pin standard and insisted on side entry cable and cable grips.).

    I have memories of reading with my shadow swaying across the book in time to the iron at my grand parents place, with a Y splitter on the end of the ceiling drop cord,  so the bulb and the iron could share the lamp holder. ('overload'  'ads' 'design' all concepts blissfully unknown.) And a light in the outside loo that came on with the kitchen light, that my uncle had added as a schoolboy in the early 1940s ,with an additional  switch in the loo itself I was told never to touch when the light was on..

    Mike.

Reply
  • Indeed, how did we all survive ? but it is a good few years , we are getting older. Earth pins on all new power sockets from about 1939, on all new lights circuits from about 1969, but these regs changes   take about half a century to work through to be common in  almost all installations in the UK.
    I was in my teens when I last fitted a 2 pin plug to something, to allow use with an existing  pre-war socket, and I'm only in my 50s - well the 2nd half of them. (one of the BS 73 type with split pins - though even in the  1970s it took me a while to find someone that still had one  -  images of the kind of thing on flame port - incorrectly listed there as BS 372 - that was a later 2 pin standard and insisted on side entry cable and cable grips.).

    I have memories of reading with my shadow swaying across the book in time to the iron at my grand parents place, with a Y splitter on the end of the ceiling drop cord,  so the bulb and the iron could share the lamp holder. ('overload'  'ads' 'design' all concepts blissfully unknown.) And a light in the outside loo that came on with the kitchen light, that my uncle had added as a schoolboy in the early 1940s ,with an additional  switch in the loo itself I was told never to touch when the light was on..