Simplified guide to cable sizes for overseas DIY installation.

I have been asked to suggest a very simple guide as to what size cables should be used for DIY installations overseas, in a hot location. This must be kept simple without the complications of de-rating for grouping or for high ambient temperatures.

I appreciate that the best advice in say the UK is "have the work done by a suitably qualified electrician" This advice is however for locations were allegedly qualified electricians are hard to find and often seem to lack basic competence.

I have therefore suggested the following.

Lighting circuits use 1.0mm cable on a 5 amp or 6 amp fuse. Earthing/grounding required if metal switches or fittings are used, but otherwise is recommended, not obligatory.

General purpose small power use 2.5mm cable on a 15 amp or 16 amp circuit. connected to a number of socket outlets of whatever type is used locally.

Dedicated circuits for larger loads, most likely water heaters, cook stoves, and air conditioners.

For a running current not exceeding 13 amps use 2.5mm cable from a 15 amp or 16 amp circuit.

For running current over 13 amps and up to 18 amps use 4mm cable on a 20 amp fuse.

For running current more than 18 amps and not exceeding 27 amps, use 6mm cable on a 30 or 32 amp fuse.

I consider that these loadings have a large enough factor of safety that no calculations are required for high ambient temperatures. Likewise modest numbers of cables grouped together will be fine at the above ratings. No allowance made for voltage drop, as the above will be fine for modest sized homes. No allowance made for different cable types, as in practice it will be whatever the local shop has in stock.

Earth loop impedance not relevant as no one knows what the earthing system is, if any,  and I doubt that anyone has an earth loop tester.I urge use of a front end RCD and a local earth rod. Colour code in line with whatever is used locally.

Parents
  • one of the BS 73 type with split pins - though even in the  1970s it took me a while to find someone that still had one  -  images of the kind of thing on flame port

    Ah I remember those well - I got my first shock from one. Someone had told me that the two wires were different - live and neutral - and you could only get a shock from the live. So when left to my own devices in my grandmother's house I'd spun the cover off one of those plugs while it was in a socket and tried to work out which was N and which was L - I couldn't tell by looking so tried touching one then the other - and was puzzled that I hadn't felt anything from either - yet it must have been live since the table lamp it was feeding was clearly on. After a few moments it occurred to me to touch both at the same time - at which point I still couldn't tell which was L and which was N but I did learn rather quickly that a shock does hurt rather a lot. Luckily I'd tried it with two fingers of the same hand, rather than one finger of each hand - even at the age of 5 or 6 my guardian angel was kept busy!

       - Andy.

Reply
  • one of the BS 73 type with split pins - though even in the  1970s it took me a while to find someone that still had one  -  images of the kind of thing on flame port

    Ah I remember those well - I got my first shock from one. Someone had told me that the two wires were different - live and neutral - and you could only get a shock from the live. So when left to my own devices in my grandmother's house I'd spun the cover off one of those plugs while it was in a socket and tried to work out which was N and which was L - I couldn't tell by looking so tried touching one then the other - and was puzzled that I hadn't felt anything from either - yet it must have been live since the table lamp it was feeding was clearly on. After a few moments it occurred to me to touch both at the same time - at which point I still couldn't tell which was L and which was N but I did learn rather quickly that a shock does hurt rather a lot. Luckily I'd tried it with two fingers of the same hand, rather than one finger of each hand - even at the age of 5 or 6 my guardian angel was kept busy!