The statement says : PEN conductor is not a live conductor but a conductor carrying an operating current.
The question is: how it is not a live conductor but carrying an operating current?
The statement says : PEN conductor is not a live conductor but a conductor carrying an operating current.
The question is: how it is not a live conductor but carrying an operating current?
Well it is not a technical reason, more of an administrative one, and only really a matter of the way that a 'live part' has been defined a few pages earlier in the document.
Live part. A conductor or conductive part intended to be energized in normal use, including a neutral conductor but,
by convention, not a PEN conductor.
no mention of carrying operating current (or not).
There is a secondary consideration, that it is only supposed to be possible to get a shock to earth from 'live' parts, and because of that earthed parts do not require insulation ' the earth' is supposed to be safe to touch. A great many things are connected to earth via a PEN such as metal switchgear enclosures. Almost any appliance or similar thing with a CPC has exposed earthed metal parts that are not insulated, and to do so retrospectively would be impractical, and arguably un-necesssary,
To re-define a PEN as a live conductor would require a complete change in the treatment of earthed metalwork on TNC-s supplies.
Note that in much earlier versions of the regulations a neutral conductor was not considered a live part either, so things like concentric cables with neutral armour were considered to be safe against penetration, and metal at neutral potential was not always insulated.
Mike
Well it is not a technical reason, more of an administrative one, and only really a matter of the way that a 'live part' has been defined a few pages earlier in the document.
Live part. A conductor or conductive part intended to be energized in normal use, including a neutral conductor but,
by convention, not a PEN conductor.
no mention of carrying operating current (or not).
There is a secondary consideration, that it is only supposed to be possible to get a shock to earth from 'live' parts, and because of that earthed parts do not require insulation ' the earth' is supposed to be safe to touch. A great many things are connected to earth via a PEN such as metal switchgear enclosures. Almost any appliance or similar thing with a CPC has exposed earthed metal parts that are not insulated, and to do so retrospectively would be impractical, and arguably un-necesssary,
To re-define a PEN as a live conductor would require a complete change in the treatment of earthed metalwork on TNC-s supplies.
Note that in much earlier versions of the regulations a neutral conductor was not considered a live part either, so things like concentric cables with neutral armour were considered to be safe against penetration, and metal at neutral potential was not always insulated.
Mike
no mention of carrying operating current (or not)
Melad Al Aqra appears to be referring to 18th Edn. In 18th Amd2, we have to look at page 52: 312.1.1 where his quote may be found.