Clarification of Table A444.2

Hello folks,

Thinking about BS guidance for separation distances for EMC. 

BS EN 50174-2:2018 gives a nice formula for working out distances between power supplies /control cable, with criteria to be met. 

BS 7671 Table A444.1 gives some minimum values which I'm Ok with, as I can arrive at the same values using the criteria and formula from BS EN 50174-2:2018.

however BS7671 goes on to state that if the criteria for Table A444.1 cannot be met then Table A444.2 should be used. I find Table A444.2 more problematic as I cannot understand where the values were derived from, and it means I can't use the formula in 50147 for anything over 600A , or IT application unknown, when actually 50174 allows for both those scenarios. 

What is the source material for Table 444.2?

Why does it use obsolete nominal voltages 240 and 415V?

Why does it consider voltages (the left side of the table) for separation when EMC is current driven?

Is the 600A mentioned three phase or single phase?

Many thanks for anyone taking the time to humour me and my ruminations.

Ben

Parents
  • Well first it is important to realise this is attempting to provide very simple rules of thumb for situations that are actually almost too complex to solve based on other standards that are equally inderterminate. Clearly actually the amplitude and frequency  within  the signal cable will affect how may mV in that cable actually cause the signal system to malfunction, as will the length of the parallel sections, and in real systems the 'safe' separation may be way closer or indeed further apart than the standards suggest. Also 'how noisy' is typical mains?  3 phase or 1 phase does not come into it - we are looking at how the wire functions as an antenna for non mains frequencies, either desired ones or not.
    The 600A limit is a bit arbitrary, but is a caution that these rules of thumb do not work with very large cables and you should calculate or measure the disturbance yourself, or more likely use an armoured cable and a larger clearance or solid trunking  and not worry too much.
    Mike.

  • Many thanks Mike